Not so. Net metering can be done with one meter. It just requires the meter to have a second input connected directly from the solar inverter. Meters used in some places overseas do this.Currently under the AS3000 rules the inverter is connected to the customer side of the meter via a circuit breaker, so true gross metering (as you mention) cannot be done without a second meter that is between the inverter and the circuit breaker.
Yes you are correct, "Net" metering not only can be, but must be always done with one meter, it is claimed that Net metering can be done with multiple meters and subtractive calculations however this is incorrect, the mathematical results do not equate.
However I was talking about the requirement of Gross metering that requires "two" meters.
I suspect your reply was actually in response to my statement about "Gross" metering which you quoted I "think" you actually may have meant to say "Gross" metering can be done with one meter, referring to a meter with a second input, however this is called a "Two Element" meter and is effectively two electronic meters in one box, it is only available in single phase and is the engineering equivalent of two meters, in multiphase there is no choice but to use two meters.
Gross metering requires the meter to be somewhere between the generator and the eventual load or grid, it is usually on the supply side of the circuit breaker, with the generator on the other side in compliance with AS3000 and any state based Service and Installation Rules.
Gross Metering requires two seperate metering circuits being measured independantly, (whereas Net Metering requires a single metering circuit.)
This should not be confused with a bi-directional meter that measures energy flows in and out of the same circuit idependantly. Net meters are bi-directional, Gross meters need not be bi-directional although most have the capability.
Two element meters have been in use in Victoria for over 20 years, with most hotwater customers on the winner tariff having one, however most of these are typically not suitable for use with generation as they are not bi-directional, and Gross is not available in Victoria in anycase.
A Net meter is always a bi-directional meter, and measures energy flows in both directions, it is NOT netting off the generation from the consumption as sometimes mis-understood, the description as NET relates to the meter only measuring the "surplus" generation energy not utilised by the customers own loads.
It needs to be wired into a metering configuration consisting of only one meter (and a single element meter) to avoid other customer loads such as Slab heating etc being supplied in a partial gross arrangement, this is why many customers moving to PFIT encounter further metering work, even if they already have an SFIT bi-directional meter.
As an example:
GROSS Metering has at least two meters M1 measuring all of the customer's generation. and M2 measuring all of the customer's consumption (or a two element meter wired to achieve the same thing).
The customer will be paid for 100% of his generators output at the PFIT ie 1kW unit will produce 1KWh over 60 minutes, customer gets paid 60c/kWh. However at the same time (ie the same hour and perhaps concurrently) the customers house may be consuming load at 1.5kW, ie consuming 1.5kWh and being charged 23c/kWh - he is paid 60c but all of his 1.0kWh generation actually supplied his own loads none was delivered to the grid, and required another 0.5kWh to be delivered from the grid to feed his 1.5kWh of load, which has cost a total of 34.5c (23c x 1.5)
Nothing was supplied to the grid, but he was paid for 100% of his generation and made a profit of 25.5c.
NET metering has a single meter M1, measuring all of the customers energy delivered to the grid, and all of the customers energy delivered from the grid. If the same situation of above occurs, the 1kW output of the customers generation is consumed directly by his 1.5kW loads, and over an hour he consumes 0.5kWh from the grid to meet his remaining load.
Nothing was supplied to the grid, and he is charged for the 0.5kWh delivered from the grid at 23c/kWh ie he pays 11.5c
Of course those who own PV units much prefer Gross, however as the PFIT payment is coming from all other customers as a subsidy it doesnt seem equitable or fair.
In another example the customers Generator output exceeds his load
Generation = 1.5kWh (1.5kW generated over 1 hour)
Load = 1.0 kWh
GROSS Metering - M1 measures 1.5kWh generated and credits the customer with 90c (60c x 1.5), the load is measured on M2 as 1.0kWh and charges the customer 23c.
The customer makes a profit of 67c, yet 66% of his generation is used by himself and only 33% of his generation or 0.5kWh was delivered to the grid.
NET Metering , the M1 meter measures the 0.5kWh delivered to the grid and credits the customer with 30c (60c x 0.5), as the customers load was supplied internally by the customers own generator there is no delivery from the grid and no charges for the energy consumed by the load as it did not pass through the meter.
The customer makes a profit of 30c, and pays nothing for the energy consumed as he generated it himself.
The Victorian PFIT subsidy from all other customers is paying the PFIT customer for the energy he delivered to the grid, not what he used himself.
Regards
Sojin