My theory was that a SunnyBoy can be run (legally, with anti-islanding enabled) by using a UPS as the synch source and charging the UPS, while the UPS powered AC circuitry once it was disconnected from the meter/mains, never to disabling anti-islanding.[/quote]
Unfortunately this is only a Theory Gully , pretty much the same theory tracker posted earlier.
The fact is a SunnyBoy with or without Anti-islanding enabled will not sync to the output of a UPS.
I have mentioned earlier in this thread that the SunnyBoy's are the only GCI that will work with the Sunny Backup , they are the only inverters that understand and can be controlled with Frequency Shift Power Control by the SBU .
Putting the Backup aside for minute,
Now with Anti-islanding enabled as you suggest , the Sunnyboy needs to sync with the grid , it does this by measuring grid impedance , voltage and frequency , A UPS does not present itself with anything like what the Sunnyboy is expecting to see to allow it to Sync , so it never will.
Also a GCI needs to know the Grid impedance because the output is not controllable , EG: the inverter needs to be able to output everything is it making in order to sync or stay online , they don't sit there like a battery waiting for you to draw as much as you need , it is all or nothing.
Now if you were to be absolutely crazy and disable anti-islanding , the Sunnyboy will read the impedance of the UPS , It's wont test to see if it is compatible , it will see the output of the UPS as a Source to unload it's total output , The result will be an instant and unpredictable explosion guaranteed !
Not even 2 UPS's can be paralleled without a communications link to sync them together , not a feature all UPS's have.
So to the backup system again.
The SBU has can accept reverse power at it's output , another ingenious feature which allows power from the sunnyboy to be converted from 240AC via the internal charger to 48vdc to charge the batteries.
It can power loads and charge the batteries at the same time , if the batteries are fully charged it can power the loads by itself or assist the backup system to provide a continuous 9kw ( if Sunnyboy is producing maximum output).
What is most important is that in either mode the SBU needs to operate it does at all times control the output of the Sunnyboy using the Frequency Shift Power Control.
It can switch the Sunnyboy into standby mode if there is no need for it EG: batteries are full and loads are only a few hundred watts., also if the SBU for some strange was to output irregular voltage the Sunnyboy while in islanding mode still has protection not to dissimilar to anti-islanding mode to shut itself off.
Basically as has been discussed apart from it being very dangerous , there is no way to achieve what this theory proposes , as I have said plenty of times already there is NO other system that is the same or even close to the Sunny Backup , It is incredibly sophisticated technology and needs to be to do what it does.
One other thing worth mentioning and for Sojin's benefit , disabling or modifying the "Grid Guard" / "Anti-Islanding" is not a user function , so in essence while people have all these idea's about using their GCI's to test theories , it's not something that in reality they can experiment with ( thankfully ) .
Gully , The Automatic Switch box used with the SBU5000 is connected via communication cables , only the SBU5000 has the ability to control it , the SBU can't work without it either.