Summary Test Report for Compliance to Australian Standards AS4777
(Grid connection of energy systems via inverters)
Report of Tests Performed For:
SMA Solar Technology AG
TEST ITEM DESCRIPTION
Type: Sunny-Backup, SBU5000”, in grid
feed mode connected to the Grid through
“Automatic Switch Box Unit (Set M)”
Nominal Operating Voltage: 230 V
Nominal Operating Frequency: 50 Hz
Nominal Output Power Rating: 5000 W
Abstract
This summary test report provides the compliance results for the “Sunny-Backup,
SBU5000” + “Automatic Switch Box (Set M)” tested at ResLab during 26th May to 28th
July 2008 for SMA Solar Technology AG for compliance to AS4777. The full test results
are reported in the ResLab REP-RL0804-T-0001 rev 0.doc
ResLab Test Report Number: REP-RL0804-T-0002 Rev A.Doc
Compliance to AS4777:
The EUT complies with the requirements of AS4777.2 and AS4777.3 as per section 3.1
and 3.2 of this report in the following modes:
a. ““Sunny Backup SBU5000 (5000W) in battery grid feed mode “On” through “Automatic
switch box (Set M)” when no energy is fed from the PV-inverter into the grid.”
b. ““Sunny Backup SBU5000 (5000) with battery grid feed mode “OFF” and energy feeding
from the PV-inverter through the ““Automatic switch box (Set M)” into the grid”As batteries are not used for grid feed, "battery grid feed mode" is always off ( disabled )
You will see from the schematic that the PV is not connected to the grid in parallel with the backup's output , The "PV coupling contactor" is only closed during grid failure , if this was closed during normal operating it will as you say be connected in parallel with the backup output.
The Sunnyboy is only connected to the grid via the the "Automatic Disconnection Device" which is the exact same disconnection device the Sunnyboy has and uses when operating in anti-islanding mode.
The Sunny Backup does have full anti-islanding with all the same parameters as a Sunnyboy , it will disconnect from the grid for all the same reasons a Sunnyboy does , voltage / frequency to high or to low as in accordance with AS4777.
Dropping off from the Grid after 20ms on detecting 0v from the grid is not correct , yes it will disconnect from the grid if it reads 0v just like any GCI does but the 20ms time is the time it take to switch the home to backup mode , not the time it takes to disconnect from the grid under a fault condition.
Section 17 page 135 of the installation manual explains setting up the Sunnyboy for island mode , you will also be happy to notice the warnings !
Never operate your Sunny Boy directly on the grid with these settings!As soon as you set the Sunny Boy to use stand-alone grid parameters, the device
no longer meets the requirements of the applicable local standard for the
connection of generators to the low-voltage grid (AS4777). In backup systems, this function is assumed by the Automatic Switch Box in combination with the Sunny Backup 5000.