Powerstar W7 Inverter modification

Getting into the nuts and bolts of wind and solar power components, installation and performance issues, ask technical questions, answers and tips

Re: Powerstar W7 Inverter modification

Postby brucedownunder » Sun Oct 13, 2013 7:09 am

Primary winding 25mm cable.JPG
Primary winding 25mm cable.JPG (38.23 KiB) Viewed 4581 times


Hello friends,,

I've sourced the heavy thick cable ,25mm earth cable , that Oztules has used for his W7 mod.

I've wound about 9 turns, and it's driving me crazy.. It's so stiff and springy.. the next apparent problem looks like it's too thick and bulky to get 30 turns ,side by side in the core..

So, questions.

does it really matter if a few of the turns cross or lay on another in the core ,the outside will be fine ,plenty of room there.

The reason for the earth cable is it's insulation is thin. Other 25mm cable has thicker insulation .

any suggestions would be appreciated, thanks

Bruce
Primary winding 25mm cable.JPG
Primary winding 25mm cable.JPG (38.23 KiB) Viewed 4581 times
brucedownunder
Solar Evangelist
Solar Evangelist
 
Posts: 99
Joined: Wed Jul 17, 2013 8:21 pm
Location: mt.Tamborine

Re: Powerstar W7 Inverter modification

Postby brucedownunder » Sun Oct 13, 2013 7:31 am

Opps, I just had a look at Oztules mod pictures .. Yep, there are a few turns on top of other turns ,so it must be OK .. Sorry for that ,should have looked yesterday ,instead of thowing rocks at the cat ..just joking ,we don't have a cat ...lol.

next time I do this sort of thing ,I'd buy welding cable and strip off the second (outer) insulation .. would be so much easier,very flexable.

Thanks

Bruce
brucedownunder
Solar Evangelist
Solar Evangelist
 
Posts: 99
Joined: Wed Jul 17, 2013 8:21 pm
Location: mt.Tamborine

Re: Powerstar W7 Inverter modification

Postby Garyho » Sun Oct 13, 2013 7:54 am

If you go to a motor rewinder they will be able to supply the proper wire that has a much thinner insulation.
Garyho
Solar Fanatic
Solar Fanatic
 
Posts: 37
Joined: Sun Jan 27, 2013 9:46 pm

Re: Powerstar W7 Inverter modification

Postby Gordon-Loomberah » Sun Oct 13, 2013 8:05 am

Normally lacquered wire is used in transformers, which has very thin insulation. The insulation on that earth wire may well cause a bit of inefficiency, and if it gets hot, you'll have a big mess.
You really want some soft-drawn copper strapping for that job, it is easy to bend, stays put, and you could laquer it yourself if you cant find any already laquered.
http://gunagulla.com Loomberah weather and astronomy including live solar radiation intensity and UV + Gunagulla aquaponics, organic eggs and cherries
User avatar
Gordon-Loomberah
Community Moderator
 
Posts: 5762
Joined: Thu Sep 24, 2009 9:41 pm
Location: Loomberah NSW Australia

Re: Powerstar W7 Inverter modification

Postby Tracker » Sun Oct 13, 2013 11:20 am

.
Could you have got "Proper" transformer wire..
Yes - RARE - Stiff - but thin insulation..

You could wind it with string, to get the length and then just buy THAT length from someone who makes transformers (Rather than a massive roll..

I would use a rubber mallet to tap each turn into shape as it goes on..
Then when complete , a few coats of ISONEL (do I remember it right) to improve the insulation..

( Sorry - just noticed the other posts - Same-Same )

PS - Now here is a go..
Look for OLD microwaves that are LIGHT - INVERTERS - They have a special transformer for the HV (2000V), made of DOZENS of fine wires twisted like a steel cable would be - MASSIVELY Flexible.. and thus easy to use.. They are normally powering about 1000W, so the power could be in the right ballpark and you could double up in parallel.. :idea:

Inverter Wire.jpg
Inverter Wire.jpg (33.23 KiB) Viewed 4564 times


What it looks like..
..
.
Last edited by Tracker on Sun Oct 13, 2013 12:13 pm, edited 2 times in total.
Retired Engineer and keen PV experimenter - Always ready to learn and share.
2 x CMS2000 (fan cooled) GCI and SE 170W panels
1.7kW First Solar/Outback Island circuit - Peak Replacement Power
Governments won't save the world :-) They will just TAX it :-(
Tracker
Solar Crusader
Solar Crusader
 
Posts: 5113
Joined: Wed Sep 23, 2009 5:54 am
Location: SYDNEY --- EA - Network, Retailer - EA

Re: Powerstar W7 Inverter modification

Postby davidg » Sun Oct 13, 2013 11:26 am

brucedownunder wrote: I've sourced the heavy thick cable ,25mm earth cable ........... I've wound about 9 turns, and it's driving me crazy.. It's so stiff and springy.. the next apparent problem looks like it's too thick and bulky to get 30 turns ,side by side in the core..

That's a really hard way to go. There is another way, you use thinner wire and wind several lots of it on, then parallel the outputs together to ramp-up the current output, make sure you use the correct lacquered wire, and get it even around the toroid BTW there are different temp ratings for the wire use a higher temperature version.

brucedownunder wrote: does it really matter if a few of the turns cross or lay on another in the core ,the outside will be fine ,plenty of room there.

No, but like Gordon said heat is an issue and the transformer will almost certainly exceed the rating of PVC insulation pretty easily.

brucedownunder wrote:The reason for the earth cable is it's insulation is thin. Other 25mm cable has thicker insulation.

Not true all "building wire" for the mm2 size has the same insulation thickness, "earth wire" is more common at those sizes because it's used from the switchboard to the main earth stake regularly.
SPS Standalone Power System/Hybrid specialist - Store the Sun!
SELECTRONIC SPMC482-AU, 8.2kW's of Arrays
Selectronic Certified AC-Coupled Fronius 8.2kW Inverter
1900Ah 48V Bank

An OTT Genset for a house.
PVOutput Stats

Sparkys light up your life :)
User avatar
davidg
Solar Crusader
Solar Crusader
 
Posts: 2102
Joined: Sat May 05, 2012 7:38 pm
Location: Dandenong VIC- *Really don't like Power Retailers at all.

Re: Powerstar W7 Inverter modification

Postby brucedownunder » Sun Oct 13, 2013 1:19 pm

Gee, it's nice to hear the experience you guys have .

I'm perservering with the Oztules earth wire method ,she's getting better. I'm using a soft hammer very effectivally around the bends and flats,the inside will just have to cope with a bendy curve,it's not too bad.

13 turns so ,there will be "inner" turns piggybacking and laying side by side in a few turns. This will be sorted out evenly after all the 30 turns are completed and secured.

Thanks for all your thinking ..

Bruce
brucedownunder
Solar Evangelist
Solar Evangelist
 
Posts: 99
Joined: Wed Jul 17, 2013 8:21 pm
Location: mt.Tamborine

Re: Powerstar W7 Inverter modification

Postby Tracker » Sun Oct 13, 2013 1:26 pm

.
Just don't forget the temperature rating of the wire -- Likely v75..

I have felt running inverter trannies and they may have got close to that 75..
So don't be adding tape insulation over the top and that will concentrate the heat..

The Selectronic type devices incorporate temperature sensing to ensure ratings are not exceeded..
..
.
Retired Engineer and keen PV experimenter - Always ready to learn and share.
2 x CMS2000 (fan cooled) GCI and SE 170W panels
1.7kW First Solar/Outback Island circuit - Peak Replacement Power
Governments won't save the world :-) They will just TAX it :-(
Tracker
Solar Crusader
Solar Crusader
 
Posts: 5113
Joined: Wed Sep 23, 2009 5:54 am
Location: SYDNEY --- EA - Network, Retailer - EA

Re: Powerstar W7 Inverter modification

Postby brucedownunder » Sun Oct 13, 2013 1:49 pm

Thanks for the temp. advice.

Do any of you know if I can place this transformer in an adjacent steel container,only a half mtr or so away ,with ,say,very heavy battery cable for the fly-leads ?? just a thought.. and a fan , temp sensor ,etc.?

Bruce
brucedownunder
Solar Evangelist
Solar Evangelist
 
Posts: 99
Joined: Wed Jul 17, 2013 8:21 pm
Location: mt.Tamborine

Re: Powerstar W7 Inverter modification

Postby ShaneG » Sat Oct 19, 2013 6:40 am

Hi all, first post, new member - problem:
Powerstar W7, PS2024E 3000W 24VDC.
The unit is miss reading the input voltage coming from the generator and therefore not engaging the charger circuit. Example - Honda generator is outputting a constant 230VAC (Checked with 2 meters) - PS W7 detects this as 286 VAC and therefore out of range.
My question is this, is there ant way to adjust or trim the input voltage reading that the W7 is sensing.

If you guys can't help me then it's an anchor!

Thanks

Shane
ShaneG