I have a copy of the remote link monitoring software and tried it out for the first time last weekend.
before I post the data their is a bit of a long (sorry

) story.
I noticed that my generator only had a tiny sniff if diesel in the tank. This came as a shock to me as we are only at the property on weekends and have been using very little energy so why did the generator run. At first I started thinking some one has drained the tank and stolen the diesel. As it was almost full 20lt tank when we took ownership of the property Feb 1st.
I then checked the kwh meter for the generator and noticed the number had increased so the generator did run but why? We have only been using a average of 2kwh a day when we are not at the property (weekday's) and around 3 to 4kwh a day max on sat-sun when we stay there.
So I downloaded the data from the inverter to see what append and this is the event log...
Sunday, 3-Mar-2012
Time:12:06.47 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
Monday, 4-Mar-2012
Time:15:05.02 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
Time:15:05.02 Ev=210 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Overcharge adjusted
Tuesday, 5-Mar-2012
Wednesday, 6-Mar-2012
Time:13:00.11 Ev=101 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Equalize automatically initiated
Time:17:01.12 Ev= 69 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Generator started, 14 days since last run
Time:17:01.41 Ev= 0 In=10 Sh=8 Cm=0 Gn=3 Gs=0 Normal entry to synchronized operation
Time:17:01.51 Ev=103 In=10 Sh=4 Cm=1 Gn=3 Gs=0 Initial charge started
Time:17:11.32 Ev=230 In=10 Sh=4 Cm=3 Gn=3 Gs=0 Bulk charge started
Time:17:24.32 Ev=231 In=10 Sh=4 Cm=4 Gn=3 Gs=0 Absorb charge started
Time:17:47.32 Ev=100 In=10 Sh=4 Cm=5 Gn=3 Gs=0 Equalize charge started
Time:21:00.12 Ev=174 In=10 Sh=4 Cm=7 Gn=3 Gs=0 Run time completed in non-preferred period
Time:21:00.12 Ev= 0 In=12 Sh=0 Cm=1 Gn=2 Gs=0 Normal return to standalone operation
Thursday, 7-Mar-2012
Time:10:21.32 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
Time:10:21.32 Ev=210 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Overcharge adjusted
Time:13:00.11 Ev=101 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Equalize automatically initiated
Friday, 8-Mar-2012
Time:11:05.47 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
Saturday, 9-Mar-2012
Time:10:49.47 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
Sunday,10-Mar-2012
Time:11:56.17 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
Time:11:56.17 Ev=210 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Overcharge adjusted
Monday,11-Mar-2012
Time:13:53.01 Ev=112 In=12 Sh=2 Cm=1 Gn=0 Gs=0 Renewable battery float achieved, equalization deferred one day
It looks like on tue 5th march the bank didn't reach float charge as their is no event posting.Then on wednesday 6th march the generator was automatically started to perform a equalization 5pm and ran for 4hrs untill 9pm. Now from what I can make of it all . Equalization is always deferred one day if the battery reaches float charge and on tue it didn't reach float so wed the gen ran? The 14 day's from last time generator was run would have been when I manually requested it to start just to test it.
Monday and particularly tue 5th march was a shocking day for solar as we had over 200mm of rain that almost turned into a cat 1 cyclone. You can see on the shunt graph it was a shocker but the battery SOC was 92% min actually thats the lowest state of charge the battery has been ever from Feb 1st.
I will have to dig deeper into the setting to see if the gen ran just because it was time for a equalization as having the gen run for that long when the battery is at 92% is excessive to me if its going to do this every time it doesn't reach float charge.
This following data was put into excel graphs you can see data starting Sunday 4th march - Sunday 11th march. Low consumption during the week as we are not their and more on the weekends. you can also see the tue 5th low output day.
one weeks Data showing amps into the battery

Same time showing state of charge %

Same time showing bat voltage

Same time showing average load watts.
This last one is showing each days kwh consumed - produced. Now I know the graph is wrong in excel as is shows pv output over night but the totals are correct for kwh consumption I think it just gets messed up in excel. Buggered if I know how it measures potential pv output? Anyhow you can see we are struggling to consume 4kwh when we are there. We usually run the washing machine-dishwasher-espresso machine, machine,stereo,laptop-modem and lighting. The 10th - 11th we had a guest over so extra water pump usage. I honestly think when we are living there full time we could say 5kwh day would be all we would use

Ok to sum up don't like the generator

20lt of diesel cost me $30 to fill the tank from empty

I feel it isn't necessary. Ok if its starts very rarely to do a EQ charge of the bank . Perhaps it was just ready for one and it had just kept getting deferred 1 day until finally i had a low output day? How often is EQ charging needed? I feel running the gen is regular thing its silly especially with my system size and small load.
Finally I did the math and I am struggling to believe a like new kubota j108 generator could burn through $30 20 ltrs of diesel just to do a EQ over 4hrs so perhaps some one did pinch some of my diesel fuel.
kubota j108 specs.
Fuel - Diesel fuel No.2
(ASTM D975)
Fuel
Consumption at Full Load L/h (gal./h) 3.1 (0.8)
at 3/4 Load L/h (gal./h) 2.5 (0.7)
at 1/2 Load L/h (gal./h) 2.1 (0.5)
at 1/4 Load L/h (gal./h) 1.6 (0.4)
Fuel Tank Capacity L (gal.) 37.0 (9.8)
Continuous
Operation
Hours at Full Load h 11.8
at 3/4 Load h 14.7
at 1/2 Load h 18.0
at 1/4 Load h 23.1
you can see below this is the wattage data produced by the generator every sample taken every 15min over the 4hr run time. So it ran roughly at 1000w its 8kva so thats under 1/4 load on the gen perhaps 6ltrs max!! hmmm perhaps some one did take some diesel . Anyhow there is a lock on it now and my 3 security cameras are now installed and watching the gen shed and the tractor.
1156w
1682w
1909w
1134w
928w
956w
1024w
995w
967w
1029w
1049w
992w
1019w
1084w
1006w
1020w